Postby mserrano » 04.09.2012, 21:22

I supose it is a simple question, but what loconet false means?

I have just competed my first GCA50 board and the red led is always ON.

I can not get to read anything (always timeout), but I do not know if it is a problem of the 101 board or the 50 board. With the config program I am able to see the 101 baord, and I think I have configured everything following the rocrail example... Maybe the problem is with the GCA 50.

Any help will be useful.

Thanks in advance,

Last edited by mserrano on 09.09.2012, 20:08, edited 1 time in total.

Postby mserrano » 09.09.2012, 09:43

Culd someone let me know if the timeout response is a problem from the MGV101 or from the MGV50?

I am attaching the rocrail.ini and the last traces... I think everything is configured as the wiki says....

Thanks in advance
You do not have the required permissions to view the files attached to this post.

Postby rjversluis » 09.09.2012, 10:31

LocoNet is your second command station in the ini so all programming commands will do to the first one: DDX.

http://wiki.rocrail.net/doku.php?id=roc ... -en#sv_iid
Best Regards, Rob.
:!: PS: Do not forget to attach the usual files.
:!: PS: Nicht vergessen die übliche Dateien an zu hängen.
[ macOS - Linux] - [ N: CBus - CAN-GCA ] - [ 0: RocNetNode - GCA-Pi ]
Site Admin

Postby mserrano » 09.09.2012, 20:07

Thanks Rob!

I was so focus on the mgv101 manual, that I did not realise on the general conf. requirements.

Best regards from Spain,